Page 2 of 2

Re: Sensor value is ouside the valid range...

Posted: Mon Aug 16, 2021 10:42 am
by mparadis
Based on those numbers I suspect you're using SENSOR_TYPE_1125_HUMIDITY instead of SENSOR_TYPE_1125_TEMPERATURE.

Re: Sensor value is ouside the valid range...

Posted: Mon Aug 16, 2021 10:46 am
by berkinet
Nope. It is set as a temperature device. I am measuring the exit pipe on a hot water system.

Re: Sensor value is ouside the valid range...

Posted: Mon Aug 16, 2021 11:23 am
by mparadis
The numbers you gave match up almost perfectly:

0.535 v/v -> 57.766 °C on the 1125's temperature sensor (or 1124)
0.535 v/v -> 61.771 %RH on the 1125's humidity sensor

I tested this on the current version of the control panel and I know you're on the latest version too. I can't think of any other reason the 1124 and 1125 enum would report different temperature values for the same voltage ratio because like you said, they use the same equation in the libraries.

Re: Sensor value is ouside the valid range...

Posted: Tue Aug 17, 2021 10:11 am
by berkinet
mparadis wrote:The numbers you gave match up almost perfectly:

0.535 v/v -> 57.766 °C on the 1125's temperature sensor (or 1124)
0.535 v/v -> 61.771 %RH on the 1125's humidity sensor...
You were right. I must have not been paying close enough attention and had selected the humidity sensor. Sorry for wasting your time :oops: